If you see an error message on your thermostat that has a code beginning with H, N or T followed by a number, here are some steps that you can take to help fix them.
Manually turn on heat, if needed
Press the button on your Heat Link to manually turn on heating:
- Google Nest Thermostat E: Press Heat Link’s button twice
- 3rd and 2nd gen Google Nest Learning Thermostat: Press Heat Link’s button once
The heating light will turn green to confirm that the heating has been turned on. This way, you can stay comfortable while you troubleshoot connection problems. If your thermostat controls your hot water tank, your hot water will also turn on.
Note: Press the Heat Link's button again to turn off heating (press twice for Nest Thermostat E).
Find your error
Select your thermostat below, then select the error code that you see on your thermostat for specific troubleshooting steps to fix the issue.
If you don’t see an error code on your thermostat, please search our library of help articles for help with other issues.
Nest Learning Thermostat
H1 or H71
An H1 or H71 error message says 'Nest can’t connect to Heat Link and won’t be able to control your heating'. In addition, the Heat Link's status light will be yellow when it’s disconnected from your thermostat.
-
Restart the Heat Link
- Hold down the Heat Link’s button until its light turns off. It should take about ten seconds.
- Release the button and wait for your Heat Link to restart.
- The status light will turn green if it re-connects to your thermostat. If the status light is yellow, continue to step 2.
-
Move your thermostat and test the connection
Your thermostat may be too far away from the Heat Link or there may be something interfering with the wireless Thread connection.
- If your thermostat is mounted on a stand (not the wall), try moving it a bit closer to where your Heat Link is installed.
- Check that there isn’t anything between your Heat Link and thermostat like a large mirror, or refrigerator. Large objects made of metal or other dense materials can block wireless signals.
- Check the wireless connection:
- On your thermostat go to Settings
Equipment. Then select Continue
Heat Link
Test.
- If the test fails, move your thermostat again and re-test. Sometimes moving your thermostat a few centimetres can make a big difference.
- On your thermostat go to Settings
-
Check your Heat Link installation
The wireless thermostat connection can be blocked if your Heat Link is installed too close to your boiler or hot water tank. Make sure that the Heat Link is installed at least 1 m (3.3 ft) away from your boiler or heating system. Reposition it if possible.
Caution: It’s important to protect you, your system and your thermostat. Turn off the power to your system at the fuse box before exposing or adjusting any wiring.
-
Reset the Heat Link to defaults
Try resetting the Heat Link and then reconnecting it to your thermostat. For complete instructions, please see How to restart the Heat Link or reset it to factory defaults.
In some cases, you may need to re-enter the Heat Link’s pairing code on your Nest Learning Thermostat. The code is a combination of six letters and numbers.
- 3rd-gen Heat Links have the pairing code on the bottom
- 2nd gen Heat Links have the pairing code underneath the cover, near the left screw hole.
-
Stop wireless interference from other electronics
- Other home products that use a 2.4 GHz wireless signal may cause interference. This includes cordless phones, baby monitors, microwave ovens and wireless security cameras. Try turning off these electronics one by one to see if your Google Nest Learning Thermostat and Heat Link are then able to establish a wireless connection.
- Once you have found out what’s causing the interference, try moving it further away from the Heat Link or Google Nest Learning Thermostat if possible and then recheck the Google Nest Learning Thermostat connection.
Note: Switching from a wireless product to one that uses cables, such as a corded phone, can solve interference issues.
Learn about wireless interference and how to troubleshoot it >
H2 or H72
1. Check the thermostat power cable, plug and power socket. If you have a Google Nest Learning Thermostat on the Nest Stand:
|
-
Note: We recommend plugging your thermostat into a socket that isn’t controlled by a wall switch to prevent accidentally switching it off.
-
You can also double check that the socket is delivering power by plugging in a lamp or other electronic device and turning it on.
2. Make sure that the display and power cable are fully seated.
|
3. Check the fuse box
- Check the fuse: It’s possible that the fuse controlling power to your system isn’t properly seated or is blown. Re-seat or replace it as necessary.
- Make sure that the switch is set to 'on': Sometimes fuse switches can be tricky: you may think that you've flipped a switch back on, but it might not have been pushed all the way.
- Try flipping the switches that control power to Heat Link and your thermostat off and then on again.
- You can also check power on the socket that the Nest thermostat is using by plugging in a lamp or other electronic device and turning it on.
4. Contact a Nest Pro
If you’re still not able to fix the problem, contact a local Nest Pro, who can properly diagnose your heating system and your Nest thermostat.
H73
An H73 error message says, 'There is a wireless connection but OpenTherm is not detected. Check your installation'.
If you see the H73 error during installation
- Verify that your heating system supports OpenTherm. Check your system’s documentation or contact the manufacturer. There may also be an OpenTherm logo somewhere on your system.
-
Make sure that the Heat Link is correctly wired. Check that your Heat Link’s wiring against the wiring diagrams in the installation guide. If you need to move any wires, turn off power to your system and Heat Link first.
Caution: It's important to protect you, your system and your thermostat. Turn off the power to your system at the fuse box before exposing or adjusting any wiring.
-
If your system does not support OpenTherm, you will need to select On/Off boiler control instead of OpenTherm. Open Settings
Equipment
Pro Setup to change the boiler control setting.
If you see the H73 error after installation
While an H73 error most often happens during or right after thermostat installation, it can sometimes occur after you’ve been using your thermostat for a while.
-
Check that the power to your boiler hasn’t been turned off.
-
If the switch controlling power to your boiler is on, but it’s not receiving power, have a local Nest Pro check your system.
N80
An N80 error message says, 'OpenTherm requires a wireless connection but wireless isn’t detected'.
-
Restart the Heat Link
-
Hold down the Heat Link’s button until its light turns off. It should take about ten seconds.
-
Release the button and wait for your Heat Link to restart.
-
The status light will turn green if it re-connects to your thermostat. If the status light is yellow, continue to step 2.
-
-
Move your thermostat and test the connection
Your thermostat may be too far away from the Heat Link or there may be something interfering with the wireless Thread connection.
- If your thermostat is mounted on a stand (not the wall), try moving it a bit closer to where your Heat Link is installed.
- Check that there isn’t anything between your Heat Link and thermostat like a large mirror, or refrigerator. Large objects made of metal or other dense materials can block wireless signals.
- Check the wireless connection:
- On your thermostat go to Settings
Equipment. Then select Continue
Heat Link
Test.
- If the test fails, move your thermostat again and re-test. Sometimes moving your thermostat a few centimetres can make a big difference.
- On your thermostat go to Settings
-
Check your Heat Link installation
The wireless thermostat connection can be blocked if your Heat Link is installed too close to your boiler or hot water tank. Make sure that the Heat Link is installed at least 1 m (3.3 ft) away from your boiler or heating system. Reposition it if possible.
Caution: It's important to protect you, your system and your thermostat. Turn off the power to your system at the fuse box before exposing or adjusting any wiring.
-
Reset the Heat Link to defaults
Try resetting the Heat Link and then reconnecting it to your thermostat. For complete instructions, please see How to restart the Heat Link or reset it to factory defaults.
In some cases, you may need to re-enter the Heat Link’s pairing code on your Google Nest Learning Thermostat. The code is a combination of six letters and numbers.
- 3rd-gen Heat Links have the pairing code on the bottom
- 2nd gen Heat Links have the pairing code underneath the cover, near the left screw hole.
-
Stop wireless interference from other electronics
- Other home products that use a 2.4 GHz wireless signal may cause interference. This includes cordless phones, baby monitors, microwave ovens and wireless security cameras. Try turning off these electronics one by one to see if your Google Nest Learning Thermostat and Heat Link are then able to establish a wireless connection.
- Once you have found out what’s causing the interference, try moving it further away from the Heat Link or Google Nest Learning Thermostat if possible and then recheck the Google Nest Learning Thermostat connection.
Note: Switching from a wireless product to one that uses cables, such as a corded phone, can solve interference issues.
Learn about wireless interference and how to troubleshoot it >
T05, T06 or T07
You’ll see a T05, T06 or T07 error message when running a system test after you first install your thermostat.
Important: Troubleshooting for each of these errors is the same in most cases but there are specific troubleshooting steps for certain errors in some steps.
-
Run the test longer
- Many systems have a built-in delay, so it might be 5 minutes or more before your system turns on.
- If you’re testing a radiant system, electric skirting board heating or a system with radiators, it typically takes a while before you can feel the floor, baseboard or radiators getting warm. Try waiting up to 30 minutes to see if they warm up.
- The System Test will run for 35 minutes before automatically stopping. Select Keep Testing on your thermostat if needed, or restart testing by going to Settings
Equipment on your thermostat. Select Continue and then Test.
-
Make sure that your boiler and Heat Link have power
Check that the Heat Link light is on, and your boiler’s light or screen is on too. If they aren’t receiving power:
-
Check that the breaker switch or fuse that controls power to your system is set to on.
Caution: It's important to protect you, your system and your thermostat. System power should be turned off during thermostat installation to help prevent blowing a fuse, but it should be turned on for testing.
-
Also check the switches for other system components. They may have a separate switch which also needs to be set to on.
-
In some homes it’s common to turn off the boiler for the warm seasons and heating is no longer needed. So it can be helpful to double check that the boiler and the breaker switch connected to the boiler are on, and that the boiler has power.
-
-
Check that the Heat Link is wired correctly
WARNING ELECTRIC SHOCK HAZARD: Failure to turn off the power may result in serious electric shock, injury and death.
- Turn off power to your system at the breaker or fuse box.
- Pull off the Heat Link cover.
- Make sure that the wires are connected to your Heat Link correctly. Follow the installation guide’s wiring diagrams &emdash; it was included in the box with your thermostat. You can also download a PDF version of the thermostat installation guide here.
- If the wires are in the right Heat Link connectors:
- Check that each wire is fully inserted into its connector and that every connector with a wire is drawn as shown.
- Turn power to your system back on at the breaker or fuse box.
- Re-test your system. On your thermostat, go to Settings
Equipment. Select Continue and then Test.
- If there are still issues, have a local Nest Pro check your installation.
-
Steps for specific system types
Check to see if anything below applies to your system or error, then restart the system test if needed.
-
If your system has radiators (T06 error): Make sure that the radiator valves are fully open so that hot water from the boiler can enter the radiators. The valves may have been closed if the season is warm and heating isn’t needed.
-
Make sure that your programmer isn’t interfering with boiler control: If you had a programmer before installing the Google Nest Learning Thermostat, it’s important that the heating channel is disabled so that it doesn’t interfere with heating.
What to do with a programmer after installing a Nest thermostat >
-
Check your heating lever valve: If you have a manual valve to turn on heating, make sure that the valve lever is in the on position, otherwise hot water won’t flow through the heating pipes.
-
If you have a Fil Pilote system: You should have your thermostat professionally installed in order to keep you safe and avoid damaging your system or your Google Nest Learning Thermostat. Your Nest Pro may need to install an additional Fil Pilote diode (sold separately) depending on your current system. Learn more about Fil Pilote and Nest.
-
-
Reinstall your old thermostat and contact a Nest Pro
Some systems are complex and difficult to set up correctly. In addition, there may be an issue with your system. For instance, sometimes a system fuse gets blown if thermostat wires make contact with each other during installation.
-
If you’ve followed all the troubleshooting steps above, reconnect your old thermostat to your system.
-
Then contact a local Nest Pro to help you get your Google Nest Learning Thermostat connected to your system and set up correctly.
-
Nest Thermostat E
H151
An H151 error message on your thermostat says 'Nest can't connect to the Heat Link and can't control your heat'. In addition, the Heat Link's status light will be yellow when it’s disconnected from your thermostat.
-
Restart the Heat Link
- Hold down the Heat Link’s Nest button until it’s light turns off. It should take about eight seconds.
- Release the button and wait for your Heat Link to restart.
- The status light will pulse blue then turn green when it reconnects to your thermostat. If the status light is yellow, continue to step 2.
-
Move your thermostat and test the connection
Your thermostat may be too far away from the Heat Link or there may be something interfering with the wireless Thread connection.
- Try moving your thermostat a bit closer to where your Heat Link is installed.
- Check that there isn’t anything between your Heat Link and thermostat like a large mirror, or refrigerator. Large objects made of metal or other dense materials can block wireless signals.
- Check the wireless connection:
- On your thermostat go to Settings
Equipment. Then select Continue
Heat Link
Test.
- If the test fails, move your thermostat again and re-test. Sometimes moving your thermostat a few centimetres can make a big difference.
- On your thermostat go to Settings
-
Reset the Heat Link to defaults
Try resetting the Heat Link and then reconnecting it to your thermostat. For complete instructions, please see How to restart the Heat Link or reset it to factory defaults.
In some cases, you may need to enter the Heat Link’s pairing code into your Nest thermostat. Pull off the Heat Link’s cover. Remove the wire cover’s screw. You’ll find the code on the back of the wire cover. It’s a combination of six letters and numbers.
-
Stop wireless interference from other electronics
- Other home products that use a 2.4 GHz wireless signal may cause interference. This includes cordless phones, baby monitors, microwave ovens and wireless security cameras. Try turning off these electronics one by one to see if your Google Nest Learning Thermostat and Heat Link are then able to establish a wireless connection.
- Once you have found out what’s causing the interference, try moving it further away from the Heat Link or Google Nest Learning Thermostat if possible and then recheck the Google Nest Learning Thermostat connection.
Note: Switching from a wireless product to one that uses cables, such as a corded phone, can solve interference issues.
Learn about wireless interference and how to troubleshoot it >
H152
An H152 error message on your thermostat says 'The power to this thermostat is off'. In addition, the Heat Link's status light will be yellow when it’s disconnected from your thermostat.
-
Check that the plug is properly connected
- Make sure that the power adaptor is fully plugged into the wall socket.
- Also check that the USB cable is fully inserted into the power adaptor.
-
Check that there’s power to the wall socket
- If your thermostat is plugged into a switched wall socket, make sure that the switch isn’t off. You can plug in a light or other electronic device like a phone charger to test.
- Also check that the fuse in the fuse box that controls the socket is functioning properly.
-
Check that the display is properly seated
Your thermostat’s display may not be connected to the base and unable to receive power.
- Pull the display off the base.
- Line up the pin connectors on the display and the base.
- Firmly seat the display on the base. You should hear a click.
H153
-
Check your system and wiring
-
Make sure that your system is OpenTherm compatible. There should be an OpenTherm symbol on your old thermostat or receiver. You can also check your systems owner’s manual.
-
Check that your system is correctly wired, and that the OpenTherm wires are in the OT1 and OT2 Heat Link connectors. Refer to your boiler’s installation guide for wiring instructions or contact a local Nest Pro.
Caution: It’s important to protect you, your system and your thermostat. Turn off the power to your system at the fuse box before exposing or adjusting any wiring.
-
-
Check your thermostat system options
-
OpenTherm may have been selected during thermostat setup by mistake, and your system isn’t OpenTherm compatible.
-
If the error message is still on your thermostat screen, turn the thermostat’s ring to select the Setup option and press to enter setup.
To manually navigate: Go to Settings
Equipment
Continue
Setup
Continue. Then select your system type (boiler, etc.). On the next screen, change OpenTherm to On/Off control.
-
Rewire your Heat Link to correctly control your system, if needed.
-
The error message should disappear. If you’re still having trouble, contact a local Nest Pro.
-
H155
An H155 error message on your thermostat says 'Your Heat Link went offline when the batteries were low'.
- Simply pull off the Heat Link cover and replace the batteries with fresh L91 Energiser Lithium AA batteries. Important: Do not use regular alkaline batteries.
- The Heat Link should automatically reconnect to your thermostat when new batteries are installed.
H156
An H156 error message on your thermostat says 'OpenTherm connection detected but you selected On/Off control'.
Your system is wired for and compatible with OpenTherm, but the OpenTherm option wasn’t selected during setup with the Nest app. You can change this setting on your thermostat:
On your thermostat go to Settings
Equipment. Then change your boiler control to OpenTherm.
Note: If you prefer not to use your system’s OpenTherm features and would like to use On/Off control instead, connect your system’s wires to the on/off boiler control terminals on Heat Link instead of OpenTherm.
H157
An H157 error message on your thermostat says 'You need a Heat Link to control your heating with this thermostat'. This can happen if you’ve removed the Heat Link from your account, and it’s disconnected from the app.
-
If your Heat Link can’t be connected to the app, reset it to factory defaults then try connecting it to your thermostat again with the app. See How to restart the Heat Link or reset it to factory defaults.
-
In some cases, you may need to enter the Heat Link’s pairing code into your Nest thermostat. Pull off the Heat Link’s cover and find the code near the left screw hole. It’s a combination of six letters and numbers.
H158
An H158 error message on your thermostat says 'To control your home's heat with this thermostat, you'll need to reset all settings…' This can happen if you’ve removed the Heat Link from your account, and it’s disconnected from the app.
Factory reset your thermostat:
- Press your thermostat ring to open the Quick View menu.
- Choose the Settings
icon.
- Turn the ring to Reset and press to select.
- Select All Settings to reset your thermostat to factory settings.
- Begin thermostat setup with the app to connect it to your account again:
- Tap the Settings
icon on the app home screen.
- Select Add product
to start thermostat setup.
- Tap the Settings
T05, T06 or T07
You’ll see a T05, T06 or T07 error message when running a system test after you first install your thermostat.
Important: Troubleshooting for each of these errors is the same in most cases but there are specific troubleshooting steps for certain errors in some steps.
-
Run the test longer
- Many systems have a built-in delay, so it might be 5 minutes or more before your system turns on.
- If you’re testing a radiant system, electric skirting board heating or a system with radiators, it typically takes a while before you can feel the floor, baseboard or radiators getting warm. Try waiting up to 30 minutes to see if they warm up.
- The System Test will run for 35 minutes before automatically stopping. Select Keep Testing on your thermostat if needed, or restart testing by going to Settings
Equipment on your thermostat. Select Continue and then Test.
-
Make sure that your boiler and Heat Link have power
-
Check that the breaker switch or fuse that controls power to your system is set to on.
Caution: It's important to protect you, your system and your thermostat. System power should be turned off during thermostat installation to help prevent blowing a fuse, but it should be turned on for testing.
-
Also check the switches for other system components. They may have a separate switch which also needs to be set to on.
-
In some homes it’s common to turn off the boiler for the warm seasons and heating is no longer needed. So it can be helpful to double check that the boiler and the breaker switch connected to the boiler are on, and that the boiler has power.
- Make sure that your Heat Link’s batteries have a sufficient charge. Simply press the button on the Heat Link. If its light doesn’t turn on, you will need to replace the batteries with new L91 Energiser Lithium AA batteries. Do not use regular alkaline batteries.
-
-
Check that the Heat Link is wired correctly
You will need to begin setup with the app again to check the wiring:
- Turn off power to your system at the breaker or fuse box.
- Pull off the Heat Link cover.
- Make sure that the wires are connected to your Heat Link correctly:
- Reset your thermostat to defaults
- Reset the Heat Link to defaults
- Remove your thermostat and Heat Link from the app.
- Then begin setup with the app again. Make sure to answer the app’s questions accurately and closely follow the wiring instructions.
- If the wires are in the right Heat Link connectors:
- Check that each wire is fully inserted into its connector and that all wires are secured with the screws.
- Check that each wire has 6 mm (⅜") of exposed wire.
- Make sure that there is no corrosion or rust on the wires. Cut and strip the ends to expose fresh wire if needed.
- Turn power to your system back on at the breaker or fuse box.
- Re-test your system. On your thermostat, go to Settings
Equipment. Select Continue and then Test.
- If there are still issues, have a local Nest Pro check your installation.
-
Steps for specific system types
Check to see if anything below applies to your system or error, then restart the system test if needed.
-
If your system has radiators (T06 error): Make sure that the radiator valves are fully open so that hot water from the boiler can enter the radiators. The valves may have been closed if the season is warm and heating isn’t needed.
-
Make sure that your programmer isn’t interfering with boiler control: If you had a programmer before installing the Google Nest Learning Thermostat, it’s important that the heating channel is disabled so that it doesn’t interfere with heating.
What to do with a programmer after installing a Nest thermostat >
-
Check your heating lever valve: If you have a manual valve to turn on heating, make sure that the valve lever is in the on position, otherwise hot water won’t flow through the heating pipes.
-
If you have a Fil Pilote system: You should have your thermostat professionally installed in order to keep you safe and avoid damaging your system or your Nest thermostat. Contact a local Nest Pro to help you get your Nest thermostat set up correctly. Learn more about Fil Pilote and Nest.
-
-
Reinstall your old thermostat and contact a Nest Pro
The Google Nest Thermostat E is designed for DIY installation, but some systems are complex and difficult to set up correctly. In addition, there may be an issue with your system.
For instance, sometimes a system fuse gets blown if thermostat wires make contact with each other during installation.
-
If you’ve followed all the troubleshooting steps above, reconnect your old thermostat to your system.
-
Then contact a local Nest Pro to help you get your Google Nest Learning Thermostat connected to your system and set up correctly.
-